Re: Help with r404a Freezer
i think that there is a current relay in the terminal box in older scroll models to control the liquid injection into the compressor .what is your discharge pressure ,you should check that both your coils are clean and fans blowing the correct direction as 40psi at -6 room temp sounds about right
Re: Help with r404a Freezer
hi head pressure is sitting between 250 psi & 200 psi the condenser fan is cycled by a hp controller. my gauges indicate that at - 6 my back pressure should be at 58 psi. Can someone explain symptoms from havving an undersized liquid line?
Re: Help with r404a Freezer
Undersized liquid line will cause flash gas and chill the liquid line, flashing in sight glass The 3/8"is good for around 7.0 Kw at 40'C Condensing -18'C evaporating at 10 metre equivelant length, 1/2"double that.
Re: Help with r404a Freezer
Pressures seem OK,
Undersize means preesure drop, pressure drop means possible flashing, flashing means reduced mass flow flow through TEV. Reduced mass flow means, straved evap. Starved evap, low suction pressure and high superheat.
Re: Help with r404a Freezer
ok can anybody see any problems in the dissconnection of the liquid injection? surely these scrolls can run without it. Its the first time ive seen one on a unit. anyone know why i would be getting ice back on the suction line at the compressor when it gets below - 10 and before that im getting a really nice sweat back. Would it just be the suction line temp causing this. Id assume if liquid was reaching the compressor id get ice build up the whole time and not just when it gets below a certain temp.
Re: Help with r404a Freezer
You get line frozen when line is at temperature below 0°C, or sweating when line is below dew point of surrounding air.
If you have any superheat at compressor entrance, than compressor doesn't getting any liquid regardless if suction line is sweating or freezing.
Compressors manufacturers prefer 20-30K superheat at compressor entrance or else installation of suction accumulator.
Measure evaporator and total superheat (10" from compressor inlet) and we will see if that is OK or not.
Liquid injection will be required when (and if) superheat is increased and evaporation temperature is low, and therefore, mass flow is lowered.
You now have high evaporation temperature and, by description of your line, low total superheat.
That mean that liquid injection for compressor cooling is, maybe, not necessary now, but when evaporation temperature drop to -30°C or -25°C, and if total superheat is high enough, you may need liquid injection to keep compressor cold enough.
Re: Help with r404a Freezer
You have 40Psi when freezer is at -6°C.
40 PSI is -14°C saturation which gives 8K TD.
TD sound good.
You could measure superheat even when temperature is not near required if you have TXV as expansion device.
TXV keep superheat at set value. That is its job, and if it has liquid refrigerant at inlet, superheat should be maintained fairly stable.
Cover portion of condenser to get stable 200 PSI and check subcooling at TXV inlet (20 cm from TXV)
Re: Help with r404a Freezer
Ah ok will measure superheat tomorrow if temps in the room are low enough. Other than the system being old are there any reasons for this thing to take so long to get down to temp (-18) takes about 3 - 4 hours to hit -17. Thanks for all the help btw
Re: Help with r404a Freezer
Undersized for actual heat load:
- To many air changes
- Bad insulation.
- To many fresh goods.
- Not designed for freezing of goods, only for temperature maintenance
Re: Help with r404a Freezer
Quote:
Originally Posted by
jbomba
Ah ok will measure superheat tomorrow if temps in the room are low enough.
Give us full set of measurments:
Quote:
Here is a list of the temps/pressures needed to troubleshoot a system:
Evap air/water in temp
Evap air/water out temp
Low side pressure or saturation temp
Suction line temp at evap outlet
Suction line temp at compressor inlet
Cond air/water in temp
Cond air/water out temp
High side pressure or saturation temp
Liquid line temp at receiver or condenser outlet
Liquid line temp at TXV inlet
The more information provided the more accurate the diagnosis.
Re: Help with r404a Freezer
Nike, beware of normal superheat settings for LT applications, in many cases it is limited to 10K without other methods of head cooling (injection, force air etc)
Re: Help with r404a Freezer
Quote:
Originally Posted by
mad fridgie
Nike, beware of normal superheat settings for LT applications, in many cases it is limited to 10K without other methods of head cooling (injection, force air etc)
You are right.
Here it is operation envelope WITH liquid injection of Maneurop LFZ scrolls for low temperature:
http://i56.tinypic.com/1zlrqsj.jpg
Re: Help with r404a Freezer
Quote:
Originally Posted by
jbomba
... my gauges indicate that at - 6 my back pressure should be at 58 psi.
Wrong. Your P/T chart (or gauge temp scale) tells you the saturation temperature of the refrigerant, not the temperature of the freezer. The saturation temp must be lower than the freezer temp.