Hey guys iv got a little problem in one side of the room the air blows out at 19 degrees and the other 3 outlets blow at 15/14 its only a smalll room aswell and they are working of same thermostat
Printable View
Hey guys iv got a little problem in one side of the room the air blows out at 19 degrees and the other 3 outlets blow at 15/14 its only a smalll room aswell and they are working of same thermostat
I assume that this is fed from a single ducted unit?
Are the ducts insulated, are they crossing over a heat source.
Try changing the ducts over at the unit outlet, if flexible ducting is used.
Check for blockages in the unit itself. Does the 19° duct have a air leak which is allowing induced air to mix in?
Checks for LEAKS in the duct work and especially at the REGISTERS, if you have a gapo there, it will suck the ambient air from the space and chage temps, ALSO if your evap is not fully charged and your return air spilts off LESS that 5 feet from the airhandler, THEN that COULD BE your problem to begin with. PLEASE let me know what you find, I would lOVE to know this one. but sounds to me like a vacuum is being created.
Lots of luck,
"NEVER ASSUME IT IS ONLY ONE THING"
hey guys thanks for your replys it seems after further inspection that two are wired to the thermostat in next room they were obviously installled by a mongo
You still haven't told us what type of system it is.
Ducted, splits. ??
...............................
nothing smart was there