problem for Mitsubishi compact ceiling cassette
Hi I got a problem from my client, his heat pump is working for about 1 hour then stop, same thing happen several times each day, then he need to press the on button to start again. From the control PAR-JH240KA, I press the "check" button, the code P8 is come on, please anybody can help me for the above problem.
Otto
Re: problem for Mitsubishi compact ceiling cassette
P8 is an outdoor fault code. It could be anything from a thermistor to a faulty contactor. It's not specific, problem is at your outdoor.
eire1
P8 tells you that you have a device active at the outdoor unit and the outdoor has registered the fault ,this does not necessarily mean the fault is with the outdoor unit !
For example dirty filters can trigger a P8.
Stu
Hi all of the helper,
I will try to have a look the outdoor unit, because this is a chinese restaurant, the outdoor unit just above the roof and may be just beside the kitchen exhaust fan. So if it is happen, can i just cleaning the thermistor or I need to replace it, and please kindly advice how to check the thermistor is working properly.
Otto
If it has them, check the LEDs of the outdoor unit, they will tell you more.
Hi Brian,
Thanks for your help, I will check the LED and let you know later.
Otto