Hot Gas vs. Electric Defrost
I was all excited about fixin' up my customers meat warehouse when his 10 HP condenser went out. The original box design is 35degF, but now we're going to design at 28degf. AS such, the existing system employees air defrost unit coolers.
Since there is no existing electric heat circuit at the unit cooler locations, I was dreaming of three 7.5 HP R-404A systems @50,000 BTUH ea. utilizing hot gas defrost. My reasoning was fewer electrical components to have to service while standing on the lift 25 feet in the air, and simplifying the installation.
After confirming my load calculations with Bohn engineering, I had already decided on BHG450 unit coolers, and asked "Glen" if he'd recommend C.U.'s. He first stated that Bohn only incorporates Hot Gas in their racks. But he justified utilizing electric defrost instead by stating that that the ELECTRIC is less maintenance, irregular defrost patterns of hot gas, and that electric heater service typically does not exceed min. circuit ampacity of the C.U. (so that by utilizing defrost relay lockout switches, there is no consideration for higher rated or additional electrical service for the heaters).
What do you think? Is Glen just selling the BDT condensers, or does that seem reasonable to you?
Re: Hot Gas vs. Electric Defrost
Quote:
Originally posted by herefishy
My reasoning was fewer electrical components to have to service while standing on the lift 25 feet in the air, and simplifying the installation.
But he justified utilizing electric defrost instead by stating that that the ELECTRIC is less maintenance, irregular defrost patterns of hot gas,
Having both in a coldstore, hot gas is by far the easiest to look after and you are not hanging off a wobbly platform in order to do the work. :D
Irregular heating of coils with hot gas defrost can be cured with some cheap and intelligent mods and fixes once you sus out where the cold spots are.
I increased cycle times from 30 minutes to 2 x 45 minute periods per day and insulated the casing of the coolers with 50mm thick polystyrene to reduce heat draining away and to keep it where it was needed.
The bigggest problem was a human one - telling the drivers to shut the #*!@"! doors to the store.
The only other possible snag with hot gas defrost is the pipework subjected to the freeze \ thaw action. If the brazed joints aren't right, they have been known to split. If you use steel, they corrode fairly quickly if not adequately protected.
Steve
Re: Hot Gas vs. Electric Defrost
I like hot gas defrost when extenuating surcumstances push you that way. I ussually install HG when there is not enough space in the electric service panel. The best part is when I lose the contract and the new people can't work on HG. Makes me look even better than I am.
I do not understand the floating head part. The gas never goes to the condenser. Head will be very low everytime. I must be doing something wrong.
Long defrost times is another area where I am confused. I use short defrost times to prevent liquid slugging with HG.
Re: Hot Gas vs. Electric Defrost
Hi,
Well, over the past couple of years (since this thread originated), I've accepted as good practice the utilization of auxiliary switches on the compressor contactors to enable and disable heat relays (contactors) for defrost heater control.
As long as the compressor and heaters are not "calling" at the same time, there is no need for additional (seperate) electrical service for the heaters and condensing unit. In my experience, I have not found a low temp system in which the electrical requirements for electric defrost exceeded the compressor's requirements.
Cheers!
Re: Hot Gas vs. Electric Defrost
Hello,
PHEnergy here, I'm new! and I only got into the Refrigeration Industry five years ago because it consumes so much Electrical Energy, and my Company reduces Electrical and Natural gas Bills for high Energy consumers. :)
Since Electric Heaters Consume less Electrical energy than the Condensing Unit, Which MUST run to provide the Hot gas I tend to go for electric. It is also easier to control.
But I would like to start a new thread here, one off my sub contractor's tech, just added Capella Oil (Texaco 68) to a newly commisioned blast freezer system using R404A, I Believe there are serious problems to follow. He says he will convert to the more expensive oil POE after a week, is R404A compatible to Capella? if not, how do we go about correcting the error, will we lose all the newwly installed R404A gas? the system demanded 9 x 24Lbs Cylinders of refrigerant. I am now seeing a dark brown cloud in the upper third of the sight glass. the system was started only Yesterday.
Re: Hot Gas vs. Electric Defrost
Hi PHEnergy.
Texaco 68 is air compressor oil
Look here and see the mistake you have made.
http://www.selectlubricants.com/manufacturers/Texaco/
POE was the right oil for the job.
Chemi :)
Re: Hot Gas vs. Electric Defrost
Quote:
will we lose all the newwly installed R404A gas?
I think the answer is YES. :eek:
And it will cost you to clean the system. If you stop now you may not lose the compressor but - hey, no promises.