Can anybody please tell me about the various tests conducted on the chilled water FCU's
Also How these tests are conducted.
Dear Munesh,
I think you would like to acertain the capacity of the FCU for air conditioning application.
FCUs are normally cross flow type heat exchangers and you can simply define the capacity by heat balance equation.
1. Water Side: Q(W)=Mass Flow Rate of water X Sp.Heat X Temp. Diff. of water at inlet & Outlet
2. Air Side: Q(A)= Mass Flow Rate of Air X Enthalpy Diff. of air at inlet & outlet.
3. See that Q(W) equals Q(A) for perfect design.
Thanks for your reply. I came to know of various tests but need to ascertain how these are carried out.
I) Air Volume Test
II) Cooling & Heating Capacity Test
III) Condensation Test
IV) Dielectric Test
V) Insulation Resistance Test
VI) Sound Level Test
VII) Vibration Test
VIII) Protection Devices test
Can anyone help me with how these can be conducted, Any special equipment or testing device required etc.
I could Lay hands on
Dielectric Test: Measures Current Leak when the phase and neutral are short circuited
Insulation test: Measures resistance wheh the phase and neutral are short circuited. Measured with a megometer. Measurements in Ohmic values.
Any additions
I) Air Volume Test
Test rig comprising ductwork to simulate actual duct resistance. Airflow measured via pitot-static tube and manometer.
Lots of thermometers ?
Stop watch, liquid measuring scale, psychrometric chart.
IV) Dielectric Test
Sound level meter and testing chamber.
VII) Vibration Test
Test bed and vibration analysis meter.
What sort of devices are you meaning?
thanks a Lot Brian & Varde