Re: McQuay Chiller Problem
If the compressor's name plate is being removed some how, you need to use the chiller model number to identify the compressor's model and then the amount of oil and the grade . Usually refrigerant oils are chosen according to compressor temperature, evaporator temperature, and kind of refrigerant used.
Re: McQuay Chiller Problem
Re: McQuay Chiller Problem
Thanks goshen. Daikin finally got back to me as well.
Cheers
Re: McQuay Chiller Problem
Quote:
Originally Posted by
philpsy
Newbie - 1st thread yeww. .
Having problems with McQuay Chiller ALS F 212.2 SE LN. Got 2 screw compressors - I'm trying to find the grade of oil in them - IOM Manual says to check the nameplate on the compressor but there is nothing there. I dont want to have to wait or pay for an oil sample as I need to get it running.
Daikin are being Homo's about it they said all I can do is place a Service Call because they dont have a Tech Support for McQuay Chiller... GRRRRRRR!
Anybody Help??
call this number and talk to Shane Eastland 763-553-5330 he will help you or get you to the right people. He is McQuay Tech Support. make shure you have the mod.no. and ser.no.
Re: McQuay Chiller Problem
Philpsy,
Details should be on tag tied to oil seperator, if not use.
Emkarate ICI RL68H.
Available from Airefrig in Australia
Regards
MQFS OZ
Re: McQuay Chiller Problem
Emkarate ici rl68h is the correct oil. You need about 10 lt to 15 lt max .