    mbc

    Re: Oil separator blocked

    Hi

    for action of HP it needs short time
    if it blocked during this time our head pressure goes up
    I saw about 400 psi .

    mbc 24-11-2017, 07:55 AM Go to last post
    Grizzly

    Re: Oil separator blocked

    But not if the blockage is before the HP switch!

    What is in between the discharge outlet and before the switch?
    (Which is what the

    Grizzly 24-11-2017, 07:17 AM Go to last post
    Segei

    Re: Freezer floor heating and sub cooling

    I don't think that it is good idea. This approach has many minuses. I would install heat exchanger. Liquid refrigerant at condensing pressure on one side

    Segei 24-11-2017, 04:25 AM Go to last post
    Glenn Moore

    Re: Oil separator blocked

    Agree with Ranger the HP safety should shut the machines down well below 500 psi .If the impingement mesh tubes in the seperator became blocked to that

    Glenn Moore 24-11-2017, 12:56 AM Go to last post
    RANGER1

    Re: Oil separator blocked

    You would think high pressure safety would/should shut machine down before 500psi???

    RANGER1 23-11-2017, 09:16 PM Go to last post