  • Pumping Liquid Refrigerant- what will work?

    Hey Guys-

    So im working on a new project, and trying to pump liquid refrigerant(134A) with a Delta P of 375 PSI, up to 510 +- Flow rate will be between 14-18 GPM. I am having a difficult time tracking down a pump. At first thoughts, i was looking for a gear pump, but people advised me that would not be the best. I received a quote on a Regen turbine pump for 16K USD. That is way too much for this project. I know vane pumps are used regularly at lower pressures, but i believe that may be the best for my application, if one can accommodate high pressures.
    Any thoughts you may have are appreciated.

    Thanks,
    This article was originally published in forum thread: Pumping Liquid Refrigerant- what will work? started by dc_Death View original post
    Comments 11 Comments
    1. TonyViet's Avatar
      TonyViet -
      ..........
    1. den052's Avatar
      den052 -
      Vane pumps can work at hydraulic pressures up to at least 3000psi that I know of. A power steering pump on a car is usually a vane pump. I used to test those at 3000psi, as the PS system pressure range is 500-3000psi.
    1. den052's Avatar
      den052 -
      Also don't know why a gear pump wouldn't do unless there is not enough lubrication in the 134A refrigerant. Are you pumping pure 134A, or mixed with oil?
    1. Aurel STDL's Avatar
      Aurel STDL -
      This is proposal organic rankine cycle with R134a as working fluid.The overlal efficiency is mostly affected by the pump efficiency. There is no available high efficient pump on the market to pump 0,01ml/h of R134a at pressure difference 9.55 bar.
      I would apreciate any suggestion regarding the pump with higher efficiency ratio at this scale.
      Microgenerationconcepts

    1. Aurel STDL's Avatar
      Aurel STDL -
      Small correction regarding pump performance. It should pump 0.01m3/h.
    1. bfrauenheim's Avatar
      bfrauenheim -
      Check out SERO Side Channel pumps. They offer flow rates and heads in the range that you require.
    1. Aurel STDL's Avatar
      Aurel STDL -
      Quote Originally Posted by bfrauenheim View Post
      Check out SERO Side Channel pumps. They offer flow rates and heads in the range that you require.
      Thanks for your recomendation, but they have to big flow rate.
      I am looking for a pump with 0,01 m3/h and to be able to reach 9,55bar pressure difference.
    1. shooter's Avatar
      shooter -
      10 liters /hour is very small, what is aplication?
      use small piston pump, when speed is reduced even gascompressor can be used.
    1. Aurel STDL's Avatar
      Aurel STDL -
      Quote Originally Posted by shooter View Post
      10 liters /hour is very small, what is aplication?
      use small piston pump, when speed is reduced even gascompressor can be used.
      I have used a solenoid pump. It works on same principle as a piston, but with solenoid instead of motor. The disadvantage is its very low efficiency.
      Here is a description of the application.
      http://www.microgenerationconcepts.c...-cycle-concept
    1. zeotrope's Avatar
      zeotrope -
      Hi,

      getting such a pump is not so difficult, price is quite high ... try

      speck pumps www.speck-pumps.com
      sihi Halberg pumps www.sterlingsihi.com
      lederle hermetic www.hermetic-pumpen.com

      they all have pumps for 4m/h 10 bars ... but there are no cheap pumps for this purpose ...
      I used their pumps for commercial refrigeration with R134a

      greetings from Germany
    1. thel33tone's Avatar
      thel33tone -
      Greetings from USA, i have successfully created a sustainable liquid refrigerant pumping system that incorporates a sealed pump design. It is currently in use in a medium sized refrigeration system, in cool weather it saves an incredible amount of electric near 30% according to the amp-meter. It incorporates liquid injection pre-condensor, and a plc controlled pump combined modulated via pressure differential sensor data. It allows the head pressures to run near 70psig with NO flash gas present. If anyone serious is interested in partnering with me contact me and i will show you what progress has been accomplished. Not to sound bigheaded but for purpose of explanation I have basically done what Hysave could not do in a cost effective more applicable way.
  • Recent Forum Posts

    Makeit go Right

    Re: Moth balled site

    Pump down sounds better than reclaim all the gas, thinking about it. Add say 8-10yrs in stasis, maybe R410a will be a banned refrigerant by then (gulp)

    Makeit go Right 24-05-2019, 08:47 AM Go to last post
    Tycho

    Re: Moth balled site

    Hi Kirky,

    Here's a worst case since you didn't provide any more than "aircon stood unused for a unknown period of time":

    Tycho 24-05-2019, 01:03 AM Go to last post
    RANGER1

    Re: Inverter AC efficiency at different speeds

    Some articles in general.
    I think also important that unit is sized correctly so it runs in low to mid range, most of the time.
    The higher

    RANGER1 23-05-2019, 08:46 PM Go to last post
    frank

    Re: Inverter AC efficiency at different speeds

    I would assume that it is most efficient when it is at low speeds, as this state only occurs as the system approaches set point. As set point nears, the

    frank 23-05-2019, 08:03 PM Go to last post
    coolguy4

    Inverter AC efficiency at different speeds

    I have a dumb question about the efficiency of an inverter AC, such as a ductless mini split. Basically, my question is in general at what capacity is

    coolguy4 23-05-2019, 07:44 PM Go to last post