  • ? about hydrocarbon gas

    i am thinking about starting to learning a bit about hydrocarbon gases to save money. can any one tell me what the difference between r290a and lpg is . can any one tell me why u cant just use pure lpg in a fridge all u would need is a pt chart for it. does lpg have more moister in it
    because from what i can work out it seems to work fine we tried it in a domestic fridge and ran fine for 4 years
    This article was originally published in forum thread: ? about hydrocarbon gas started by iceberg1988 View original post
    Comments 3 Comments
    1. chillerman2006's Avatar
      chillerman2006 -
      R290 is a CLEAN refrigerant

      lpg ect is dirty, moisture and non condensables and foreign bodies

      also regrigerant grade hydrocarbons are stenchless/no smell

      as the stenching agent is absorbed by drier cores

      would say you got lucky with your domestic

      R's chillerman
    1. chillerman2006's Avatar
      chillerman2006 -
      waste of thread

      have replied to your article

      R's chillerman
    1. chillerman2006's Avatar
      chillerman2006 -
      have now found you have had all the answers here

      http://www.refrigeration-engineer.co...ydrocarbon-gas

      and these dont change by reposting the same question

      thread should be deleted really

      R's chillerman
  • Recent Forum Posts

    cadwaladr

    Re: VRV III - 4 way valve replacement

    it's like working on a musical instrument sometimes stand back and dismantle the problems,as I said ealI erlier transport stuff is tough but cutting out

    cadwaladr 26-04-2018, 03:03 AM Go to last post
    doorswing

    Re: mitsubishi splits faulty after generator test

    found units had a unmarked finder type relay lying in the bottom of the master unit,after unplugging the units ran
    for 30 secs then stopped.Tried

    doorswing 25-04-2018, 10:42 PM Go to last post
    Brian_UK

    Re: VRV III - 4 way valve replacement

    I have in the past removed the fans and tope covers to improve access into some of these units, might be something to think about.

    You can

    Brian_UK 25-04-2018, 10:23 PM Go to last post
    VRVIII

    Re: 4th wire on Daikin VRV inverter compressor.

    Hi,
    The N wire provides a feedback signal to the inverter board which is used to detect the rotor position.
    Itís unlikely a problem with the

    VRVIII 25-04-2018, 09:17 PM Go to last post
    Harvestman

    Re: VRV III - 4 way valve replacement

    Unfortunately the company I work for stupidly negotiated a fully inclusive contract upto a vast sum. The manager decided that as the company has to pay

    Harvestman 25-04-2018, 08:54 PM Go to last post