    i am thinking about starting to learning a bit about hydrocarbon gases to save money. can any one tell me what the difference between r290a and lpg is . can any one tell me why u cant just use pure lpg in a fridge all u would need is a pt chart for it. does lpg have more moister in it
    because from what i can work out it seems to work fine we tried it in a domestic fridge and ran fine for 4 years
    This article was originally published in forum thread: ? about hydrocarbon gas started by iceberg1988 View original post
    Comments 3 Comments
    1. chillerman2006's Avatar
      chillerman2006 -
      R290 is a CLEAN refrigerant

      lpg ect is dirty, moisture and non condensables and foreign bodies

      also regrigerant grade hydrocarbons are stenchless/no smell

      as the stenching agent is absorbed by drier cores

      would say you got lucky with your domestic

      R's chillerman
    1. chillerman2006's Avatar
      chillerman2006 -
      waste of thread

      have replied to your article

      R's chillerman
    1. chillerman2006's Avatar
      chillerman2006 -
      have now found you have had all the answers here

      http://www.refrigeration-engineer.co...ydrocarbon-gas

      and these dont change by reposting the same question

      thread should be deleted really

      R's chillerman
  • Recent Forum Posts

    Shibhrac

    Re: Thermo King Spectrum SB mutitemp not cooling

    If all components are in good state and all setting parameters are in correct position as you said and also you are sure about the functionality of solenoids

    Shibhrac 19-08-2018, 07:39 AM Go to last post
    Glenn Moore

    Re: Accumulator frosting and dropping suction pressure Caterpilar Machine

    Check that the capillary tube (expansion) is away from any heat source or touching anything hot. The capillary tube must be full of liquid refrigerant

    Glenn Moore 18-08-2018, 09:01 AM Go to last post
    al

    Re: Accumulator frosting and dropping suction pressure Caterpilar Machine

    Sounds like an evap issue as others have stated, although as Cad suggests pull the charge, i presume you've not been adding oil to it?

    al 17-08-2018, 10:10 PM Go to last post
    meekertim

    Re: Thermo King Spectrum SB mutitemp not cooling

    no codes at all, screen shows 00! I believe this is because the pretrip individually tests evaps one at a time so if zone 2 is in null and it is testing

    meekertim 17-08-2018, 04:30 PM Go to last post
    RANGER1

    Re: Accumulator frosting and dropping suction pressure Caterpilar Machine

    Dirty or frosted evaporator?

    RANGER1 17-08-2018, 02:42 AM Go to last post