  1. 9 superheat & subcooling scenarios

    Quote Originally Posted by nike123 View Post
    • LOW CHARGE = High superheat. Low suction pressure, indoor TD, subcooling, head pressure & compressor current draw.
    • OVER CHARGE = Low superheat. Normal indoor TD. High suction pressure, subcooling, head pressure & compressor current draw.
    • LOW INDOOR AIR FLOW = Low superheat & suction pressure. Low to normal head pressure. High indoor TD. High to normal subcooling. Not much effect on current draw.
    • MILD LOW OUTDOOR AIR FLOW = Low superheat & subcooling. High suction
    ...
    Categories
    Uncategorized


  2. Extending torque wrench correctly

  3. What is the purpose of having the capillary tube soldered to the suction line.

  4. Refrigerant circuit animation video

    Here is nice explanation:

    Updated 28-09-2013 at 08:10 AM by nike123

    Categories
    Uncategorized
  5. Major differences between R22 and R410 kompressors

    Quote Originally Posted by nike123 View Post
    There are three distinct design differences between and R-22 and R-410A compressor:
    • Different Oil: Because mineral oil, normally used in R-22 compressors, is not miscible with HFC refrigerants such as R-410A, Copeland uses a synthetic Polyol Ester Oil (POE) in R-410A approved compressors.
    • Reduced Compressor Displacement: A pound of R-410A has approximately the same heat carrying capacity relationship to R-22 as R-22 has to R-12, therefore, the compressor displacement has to be reduced
    ...