You arrive to a job-site to find an already irritated customer awaiting your visit. You learn that their plant room shut down last Friday and nobody realized it until Monday morning. So you start to investigate the root cause of the problem and then it becomes apparent to all that your company is at fault. How do you proceed? The customer wants answers and they're looking at you! Before you start to talk, stop and think. The last thing you need is for this conversation to go ...
Originally Posted by nike123 LOW CHARGE = High superheat. Low suction pressure, indoor TD, subcooling, head pressure & compressor current draw.OVER CHARGE = Low superheat. Normal indoor TD. High suction pressure, subcooling, head pressure & compressor current draw.LOW INDOOR AIR FLOW = Low superheat & suction pressure. Low to normal head pressure. High indoor TD. High to normal subcooling. Not much effect on current draw.MILD LOW OUTDOOR AIR FLOW = Low superheat & subcooling. High suction ...
Originally Posted by nike123 http://www.freeinfostuff.com/TorqueE...eExtension.htm
Originally Posted by nike123 http://docs.lib.purdue.edu/cgi/viewc...&context=iracc
Here is nice explanation: