  1. Superheat and subcooling.

    Quote Originally Posted by nike123 View Post
    Superheat of TXV should be adjusted at commissioning or replacement of valve.
    Superheat should be adjusted at about 65% of evaporator design TD when ambient temperature of cooling equipment is 1-2 K near design temperature.

    http://maleki-hvac.ir/Portals/0/Kuba...ructions_2.pdf

    Subcooling should be adjusted with refrigerant charge when ambient temperature is near design temperature. Condenser could be partially covered to get that design condensation temperature.
    ...
    Categories
    Uncategorized


  2. Presure-Entalpy chart explained

  3. 9 superheat & subcooling scenarios

    Quote Originally Posted by nike123 View Post
    • LOW CHARGE = High superheat. Low suction pressure, indoor TD, subcooling, head pressure & compressor current draw.
    • OVER CHARGE = Low superheat. Normal indoor TD. High suction pressure, subcooling, head pressure & compressor current draw.
    • LOW INDOOR AIR FLOW = Low superheat & suction pressure. Low to normal head pressure. High indoor TD. High to normal subcooling. Not much effect on current draw.
    • MILD LOW OUTDOOR AIR FLOW = Low superheat & subcooling. High suction
    ...