I am not an AC expert but I am a mechanical engineer with some theoretical knowledge of the basics. I have a 3,000 ft2 masonary house in Brazil in which I had installed a Hitachi central air system. I have double-pane glass and 4" of insulation on the ceiling slab.
The contractor calculated 8T of cooling and installed 2 x 5T heat-pump systems. These have given nothing but trouble, tripping on high pressure in summer and low pressure in winter. I am also disappointed in their performance when they do run.
I am interested in some basic guidelines as follows:
1. What is the typical temperature drop across the evap. in cooling mode?
2. What is the typical rise in temp across the condenser (indoor unit) in heating mode?
3. On a typical summer day with outside DB at 90F and indoor WB at 70F what should the typical refrigerant suction and discharge pressures be (R22)?
4. What is the typical temperature of the evaporator coil during cooling under the above conditions?
These systems do not have TEV's but capillaries instead. There is a check-valve around the capillaries in the condensing unit (cooling bypass) but no check around the capillaries in the indoor unit.
Any help will be appreciated. JCole
The contractor calculated 8T of cooling and installed 2 x 5T heat-pump systems. These have given nothing but trouble, tripping on high pressure in summer and low pressure in winter. I am also disappointed in their performance when they do run.
I am interested in some basic guidelines as follows:
1. What is the typical temperature drop across the evap. in cooling mode?
2. What is the typical rise in temp across the condenser (indoor unit) in heating mode?
3. On a typical summer day with outside DB at 90F and indoor WB at 70F what should the typical refrigerant suction and discharge pressures be (R22)?
4. What is the typical temperature of the evaporator coil during cooling under the above conditions?
These systems do not have TEV's but capillaries instead. There is a check-valve around the capillaries in the condensing unit (cooling bypass) but no check around the capillaries in the indoor unit.
Any help will be appreciated. JCole