PDA

View Full Version : Daikin FXSQ100M8



SkyWalker
02-10-2007, 06:32 PM
hi guys was commissioning this indoor unit today testing pump ect.... Found myself taking off the supply ducting to poor water into the drip tray to make the pump run...

Is there an easier way to test the pump? maybe from the board, as when doing alot of units this would get slightly frustrating?

also how much water should it take until the float is made and the pump runs? approx?

BigJon3475
02-10-2007, 06:42 PM
http://www.daikinac.com/residential/docsEngineering.asp?sec=docs&page=58

Did you try looking on the site.

SkyWalker
02-10-2007, 07:05 PM
thanks for link to site will come in handy! as for testing the pump was trying to find out how you guys go about testing internal pumps?

The Viking
02-10-2007, 07:23 PM
The easiest I found is with a Garden Sprayer. Just fill with water, pump up the pressure and spray the coil until the pump starts.

It might be tricky on ducted units but it's normally a small hole somewhere and the lance for a garden sprayer are less than 1/2"

superswill
02-10-2007, 07:23 PM
i know most mitsubishi unit have a small side plate that can be removed in order to pour water in,i mainly use a 5L spray doc with a small lenght of 3/8 hose on for test internal and external

Andy AC
02-10-2007, 07:48 PM
Haven't the daikin ducted units got a removable black plastic plug on the side of the unit by the drain outlet?
you may be able to run the pump from the controller, however I am not familiar with Daikins these days, I know you can on a MHI. Anyway that wouldn't help you if you couldn't get the water into it in the first place;)

Andy

frank
02-10-2007, 08:30 PM
Haven't the daikin ducted units got a removable black plastic plug on the side of the unit by the drain outlet?

Spot on Andy - that's exactly what the inspection cover is for. I'd put at least 2 litres into the unit to test the lift pump and/or any subsequent tank pump.

One of the biggest call backs on A/C is for condensate removal problems. Special care at install stage will reap rewards later. :)

Obi Wan
02-10-2007, 08:47 PM
hi guys was commissioning this indoor unit today testing pump ect.... Found myself taking off the supply ducting to poor water into the drip tray to make the pump run...

Is there an easier way to test the pump? maybe from the board, as when doing alot of units this would get slightly frustrating?

also how much water should it take until the float is made and the pump runs? approx?

Hello Skywalker,

See the attached JPEG from the installation manual for the FXSQ-M indoor units.
There is a hole just below the drain outlet for you to pour water in.

If you just want to run the lift pump then put the indoor unit in the “Fan Only” mode, then press the “TEST” button repeatedly until you see “TEST” displayed on the remote controller, then press the ON button.
The Fan and the lift pump will run for half an hour.

Otherwise use the FORCE.