HELLLO, just want your thoughts please.
i was called to a bakers today to a new OscarTielle multideck which was blowing fuses on inspection i for it had 2 compressors both running ay 7.5 amp and 2 mains flexes both rated a 13a, i found the 1 flex was hot and the plug top was burning out this was due to both compressors being wired into the same mains flex which was drawing 18a and cauing the fuse to blow the other flex had only 2 amp on it, i split the load bettween the 2 flexes and all is well now but i have to check another 8 cabnets for this fault just to be safe, anybody else had this problem?:eek:
i was called to a bakers today to a new OscarTielle multideck which was blowing fuses on inspection i for it had 2 compressors both running ay 7.5 amp and 2 mains flexes both rated a 13a, i found the 1 flex was hot and the plug top was burning out this was due to both compressors being wired into the same mains flex which was drawing 18a and cauing the fuse to blow the other flex had only 2 amp on it, i split the load bettween the 2 flexes and all is well now but i have to check another 8 cabnets for this fault just to be safe, anybody else had this problem?:eek: