View Full Version : Air cooled chillers vibration isolation



vijay_study
16-09-2007, 01:00 PM
Hi,

We are into process of procuring 300TR x 6 Nos. air cooled chillers for one of our R&D centers.

The chillers are located on the terrace of the R & D center alongwith the pumps.

What is the vibration frequency range for chillers in general?

Ways and means to reduce vibration tranmission chillers to the structure?

Please guide.

Regards

Vijay Kumar

The Viking
16-09-2007, 06:19 PM
Anti vibration feets under the chiller (normally, on heavier plant, these would be an enclosed spring with bolt holes above and below) and flexible pipe and/or joints in the pipework.

narender singh
06-10-2009, 02:36 PM
first of all you check the pump alignment check if your pump alignmentis not ok than vibration occour due to dis ailgnment .and you also vibration pad use in pump frame base.

Brian_UK
06-10-2009, 08:53 PM
^^ I think that you should perhaps check the dates before you reply. ;)