PDA

View Full Version : prestcold k150/0025



fri11j
22-08-2007, 01:54 AM
can someone help me with some technical details on a prestcold k150/0025 3 phase compressor.

i suspect that it is 1.5 hp but I would really like to know the displacement in cc's

thanks guys

ckone180
22-08-2007, 02:51 AM
can someone help me with some technical details on a prestcold k150/0025 3 phase compressor.

i suspect that it is 1.5 hp but I would really like to know the displacement in cc's

thanks guys

Is that a Copeland brand?

monkey spanners
22-08-2007, 06:36 PM
Its a 1.5hp compressor. nearest one in my book is a pk15x/0025 which is the esteroil charged version. the 0025 number is the swept volume in m3/second which works out as 9.1m3 at 1450rpm. I think its a low temperature model.
Yes its a Copeland style compressor. Valve bolt threads are unf instead of unc i think. they where built in the uk (possibly elsewhere to) and badged 'Prestcold'. Prestcold started out as pressedsteel car bodies makeing panels for Rover (i think) Don't know who copied who design wise.
Some of the earliest ones ive seen where badged as pressedsteel, 40+ years old.

Jon

Electrocoolman
22-08-2007, 10:50 PM
Hi FRI11J,
Got out the trusty old books and this is what it says:

K150 / 0025
Motor HP: 1.5
Motor kW: 1.10
RPM: 1450
Cylinders: 2
Swept Vol: 8.83 m3/h
Oil Charge: 0.86 L
Net Weight: 43 kG
Suction: 5/8"
Disch: 1/2"
Max run current: (220-240/1/50) 11.0A
(360-420/3/50) 3.5A
Locked Rotor: (220-240/1/50) 43.0A
Direct Start: (360-420/3/50) 19.0A

R12: H/LBP
evap-40:740W@30C cond, 440W@50C cond.
evap 0:4650W@30C cond, 3770W@50C cond,
evap +15: 7410W@30C cond.
note: not rated higher than +5 evap/cond @50c (evap/cond@50c)

R22: M/LBP
evap -40 1060W @ 30C cond, 680W @ 50C cond,
evap 0: 6220W @ 30C cond.
note: not rated higher than -15 evap/cond @50C

R502: M/LBP
evap -40 1530W @ 30C cond, 930W @ 50C cond.
evap 0 6600W @ 30C cond.
note: not rated higher than -25 evap/cond @50C

Hope this is of use.

Adrian.

Andy W
26-08-2007, 07:13 PM
If you need to know the duty at a given evap temp, give me a shout, i still have some old charts.

amalhichem
11-12-2009, 02:45 PM
prière envoyer les document technique des compresseur PRESTCOLD model :
K100/0017 et K 150/0025
mes salutations.

old gas bottle
11-12-2009, 03:09 PM
and i have a brand fire new one,never run one the shelf gathering dust,must be 10 years old or more now.:eek:

chillled
11-12-2009, 10:42 PM
My God, i Rebuilt hundreds of these during my blue period

Moris
26-04-2010, 04:23 PM
Hi all

has anyone out there come across a Prestcold MALR150 condensing unit circa 1982, it is running a freezer on R12 I need to change the whole condensing unit but would rather leave the evaporator in situ, any sugestions (only helpful one please)
cheers

monkey spanners
26-04-2010, 05:54 PM
I'd phone climate centre technical with model numbers of both the evap and condensing unit and get them to recommend a suitable replacement.
If the evap is suitable this may be a new unit and txv for R404A. I'm not sure R134a, which would be the nearest refrigerant pressure wise, is very efficient at freezer temperatures.
I'd also change the solenoid if the system has one as they can leak with the newer refrigerants/oils after years of faithful R12 service.

Moris
27-04-2010, 07:41 AM
Thanks Monkey Spanners

I will give them a ring

regards