A/C's Heat pumps and other such "comfort" cooling you will have noticed no receiver, yet, they will use TXVs! How do they pull this off? They over size the condenser and flood 3-5 rows and use that as part of their receiver but the system becomes a critical charge system! Another reason why they can get away with it is relatively stable load once under operation.
Now, technically, any system can be don this way, a Receiver just makes charging far easier and is more forgiving to error in charging. How ever it demands a higher system charge, and is an added risk of leakage or failure point, and drives cost of production up!
A critical charge system on the other hand, reduces net system charge, less potential failure points. How ever, not forgiving to charging errors, and must be care fully charged which can be time consuming and can at times perform poorly on low ambient environments, which a receiver would other wise benefit on good sub-cooling!
So, In the end, with care full thought for design, and in a situation where evap load remains relatively stable a receiver is not required, but rather, is an option
Thats what I wrote in another forum, and to my current understanding is correct. Is this correct? What have I missed if any thing (Hard to believe I didn't if thats the case! lol)
All so what are your opinions on receiverless systems?
Now, technically, any system can be don this way, a Receiver just makes charging far easier and is more forgiving to error in charging. How ever it demands a higher system charge, and is an added risk of leakage or failure point, and drives cost of production up!
A critical charge system on the other hand, reduces net system charge, less potential failure points. How ever, not forgiving to charging errors, and must be care fully charged which can be time consuming and can at times perform poorly on low ambient environments, which a receiver would other wise benefit on good sub-cooling!
So, In the end, with care full thought for design, and in a situation where evap load remains relatively stable a receiver is not required, but rather, is an option
Thats what I wrote in another forum, and to my current understanding is correct. Is this correct? What have I missed if any thing (Hard to believe I didn't if thats the case! lol)
All so what are your opinions on receiverless systems?