PDA

View Full Version : fuji electric system



aza
20-08-2007, 04:58 PM
Hi All, Found a system today to which the outdoor unit constantly runs, fan included even when you switch the indoor unit off with the remote control???

Indoor unit model RSW-127c
Outdoor Unit model ROW-127c

Ok. Power to system- from 3pin plug to indoor unit, from indoor to outdoor, no ioslators.
Switch plug on- outdoor unit immediatly starts up- fan and compressor even though you have not turned the indoor unit on?
Switch the indoor unit on with remote everything works fine, plenty of gas, runs at 55 psi suction side.

Switch the indoor off with remote, outdoor unit continues to run, compressor switching on and off trying to circulate gas getting nowhere, result start of iceberg forming around pipe work.

Question_ with indoor off why is the power going to the outdoor unit making it run when it shouldn't be ????? Comms?? Thermistors??

Any ideas?

Aza

Andy AC
20-08-2007, 08:10 PM
Sounds like a compressor relay welded shut on the indoor pcb- new board required unless comp relay is separate from pcb.

Andy

monkey spanners
20-08-2007, 08:12 PM
Compressor/condenser control relay on indoor board contacts stuck together. If you take the board out and put a tester across the relay contacts it'll be stuck.

Jon

Brian_UK
20-08-2007, 08:12 PM
Andy AC has hit it on the head, common fault with these babies.

Brian_UK
20-08-2007, 08:12 PM
Drat, Monkey beat me to it ;) :)

aza
20-08-2007, 08:32 PM
Will check it out.

Thanks

Aza