Hi guys, just got a call from a guy at work, who is on call tonight. He got called to a restaurant with 4 indoor sanyo cassettes and one multi out door. The problem is the controller is flashing E04 ( comms error?) problem is im trying to guide him through what to do from here. Iv told him to check the basics i.e power to the outdoor, voltage of the outdoor PCB any blown fuses etc. Are there any sanyo experts around to help as the technical number for sanyo is closed until monday:eek:

superswill
17-08-2007, 07:08 PM
does this help

http://www.refrigeration-engineer.com/forums/showthread.php?t=8795&highlight=sanyo

marc5180
17-08-2007, 07:14 PM
Power to the outdoor PCB
The 0.6Ma fuse on both PCBs its soldered on
If this fuse is gone
Check the control Cable
If this is OK then There is a brown plug on both indoor and outdoor PCB's marked EMG.
This is on the off side of the fuse Make sure all cables are OK as if there is anything wrong with comms cabling this can blow the PCB if this plug is used.

Providing comms cables are OK

Change the blue comms plug with the pink and blue wires into this EMG socket on Both indoor and outdoor PCB's

If this doesn't work this snip v006 off the outdoor PCB and try again


Would it be the same on a mutli unit?

dannycool
18-08-2007, 07:44 PM
speak to someone at ICG in stockport who supply us with sanyo kit, we have found them always willing to help.

ICG-01614294800

marc5180
18-08-2007, 07:57 PM
thanks Dannycool, but i already have that number and i tried to ring them the other day but they were closed until monday.

dannycool
18-08-2007, 08:45 PM
oh right, well if you pm me your email add, i can send you a pdf of the sanyo service manual, if thats of any use.

Electrocoolman
18-08-2007, 09:15 PM
Hi Marc,
Do you know what system this is ....SAP or SPW?

Guess as you talk about a controller, it is a wired controller so that it will probably be a SPW system (SAP have Infra Red controls). Any chance of a model # ?
E04 is generally Indoor unit is detecting an error signalled from the outdoor unit: Error in receiving serial communications signal.

marc5180
18-08-2007, 11:04 PM
Hi Marc,
Do you know what system this is ....SAP or SPW?

Guess as you talk about a controller, it is a wired controller so that it will probably be a SPW system (SAP have Infra Red controls). Any chance of a model # ?
E04 is generally Indoor unit is detecting an error signalled from the outdoor unit: Error in receiving serial communications signal.

I dont know what model it is until the guy rings me back and lets me know, if it hasnt been sorted already then i expect il be called to it on monday morning.