13-08-2007, 10:23 PM
I got this service call the other day. It was a 2ton keeprite ultraquiet residential a/c system. The complaint was that the A/C doesnt shut off and runs continiously. On my inspection the pressure were a litttle low, and condenser unit was very dirty. So i topped up the refrigerant and cleaned the condenser coil.
The pressure on low side was 70psi and High Side 160Psi. with R22 refrigerant and temperature outside was about 88F. I dont know why the high side pressure is too low? Any idea as to why the high side pressure lines feel cold and has low pressure?

Brian_UK
13-08-2007, 10:57 PM
Did you do a leak test before 'topping up'?

Is the compressor pumping correctly?

The Viking
13-08-2007, 11:47 PM
If we take a step back.....

Did you connect your gauges to the service ports on the outside side of the outdoor unit?
Were both pipes lagged?(sorry never worked on these units)

If the answer to both these questions is YES, then you measured an intermediate pressure and not a true HP.

mohamed khamis
14-08-2007, 02:59 AM
I got this service call the other day. It was a 2ton keeprite ultraquiet residential a/c system. The complaint was that the A/C doesnt shut off and runs continiously. On my inspection the pressure were a litttle low, and condenser unit was very dirty. So i topped up the refrigerant and cleaned the condenser coil.
The pressure on low side was 70psi and High Side 160Psi. with R22 refrigerant and temperature outside was about 88F. I dont know why the high side pressure is too low? Any idea as to why the high side pressure lines feel cold and has low pressure?

It sounds the system has leakage, both the low-side and high-side pressure are low. It can also deduced from the low values of the condensing and evaporating temperatures 80.71F and 30F although the condenser was fouled and the ambient temperature is above the condensing temperature. So it is better to check the leakage matter firstly?.

fireandice
14-08-2007, 09:21 AM
Hi, could be a leaking reversing valve, 70psi could be high depending o room temp.

themba
14-08-2007, 12:53 PM
i would recomend that you check if the compressor pumping efficiently, and verify that there are no leaks.