View Full Version : Daikin twin split



Lippygit
25-07-2007, 11:45 PM
Does anyone know the dip switch settings for a daikin skyair twin split ? Someone prior to myself has decommissioned a twin split to be re-installed within the same building at a different level . On re-commissioning we have a UA fault ???? Too many evaps .... would appear to me that the dip switches may have been fiddled with or accidentally changed during storage. Any help gratefully appreciated .

The Viking
26-07-2007, 12:01 AM
If you give me the model number I can find out for you.

Otherwise, if you go to www.daikin.co.uk you are able to download the manual (but again, you will need the mod no)

Lippygit
28-07-2007, 06:28 PM
Problem solved , the installer added an extra cable to P1 & P2 which weren't required.