I have a york ycag36 46 d recip chiller. When it tries to start code f1 shows up for circuit 1. Circuit 2 starts and runs. F1 has several causes,low or high motor current, ext high pressure switch, micro high press sw. All are within range. Any suggestions ?

Dr._Fleck
19-07-2007, 04:27 PM
faulty pressure switch?.. Maybe?

INDIAN HEAD
20-07-2007, 12:37 PM
No external pressure switch and transducer shows same pressure as the compound guages on micro processor display

bigbadcol
31-10-2007, 09:59 PM
If the compressor is not starting and comes up F1 then the fault is caused by low(or no)current.Check the compressor fuses and check the contactor internals.

gsxr1340
31-10-2007, 11:59 PM
Hi,can you give us more info about the controls, is the micro a millenium controller