Mohammed Qasim
12-07-2007, 11:49 PM
I have a problem with a Carrier split heat pump ( made in Korea )
it works for 23 minutes then stop responding to the remote control , closing the swing and a led start flashing.
During the 23 minutes of its work nothing is wrong the temperatures ,the pressures etc . whats the possible reasons for this help please.

decrom
13-07-2007, 04:57 PM
Hi Mohammed !
If your sure that the refrigeration cuircuit is ok (normal pressure), if there is no osbstuction any where, i suggest you to check if you are having the rigth voltage:may be it's to low.Hope this will help you.
Warm regards !:)
Decrom( Cameroon)

Electrocoolman
13-07-2007, 09:40 PM
Mohammed,
Can you find the model number(s) of the system.

Also can you study the flashes of the lamp. They will probably not be purely on / off but the 'on' flashes will be grouped together followed by a longer 'off'. You need to count the number of 'on' flashes in a group.

We might be able to offer more help with more information.