Hello, has anyone had this experiance.

A Unico System with a Highcool Heat pump.

Problem! All wires from hard wired control panel via unico unit disconnected at outdoor unit, so, no communication from indoor to outdoor so it should be switched off.

But, outdoor continues to run???? from approx. 42psi on Suction side until the pressure drops to approx 17psi then the compressor cuts out pressure slowly rises, compressor starts.
This continues none stop.
Has anyone experianced anything like this??????

Brian_UK
03-07-2007, 10:58 PM
Errr, seems like LP switch is working then.

aeb200
03-07-2007, 11:11 PM
Unico controllers usually work on 24v signal - is this compatible with youre hi cool unit??

without the unico fan running the system will produce low pressure symptoms

does the system have a pump down solenoid is it letting by??
what size expansion valve have you fitted to unico coil (or is it a chilled water version)
has the system been commissioned properly??

aza
04-07-2007, 09:48 PM
This system works in cooling and heating modes, it just continues to operate after you switch the system off :confused:

marc5180
04-07-2007, 10:23 PM
Glad its not just me then, that comes across units with strange faults:D