Has anyone any experiance on any of these chillers im sure they are made in Italy. I am attending site tomorrow and will then have the model.
Any info would be good
Thanks in advance:confused:
They're made in Italy indeed, www.rcgroup.it (http://www.rcgroup.it). Not much tech info on the site, but contact to UK distributor;
EXCEL AIR CONDITIONING Ltd
Unit 33, Moor Park Industrial Centre, Tolpits Lane
WD18 9SP WATFORD HERTFORDSHIRE
UNITED KINGDOM
telephone: +44 01923 254001
fax: +44 01923 815950
e-mail: mark.hutchings@excelac.co.uk (mark.hutchings@excelac.co.uk)
Assigned areas: United Kingdom
puddleboy3
02-07-2007, 08:14 AM
Well after attending site and contacting UK dist, with the model numbers and serial numbers. I have been told that they dont produce any service/installation information and the best bit is that they charge you £25 for wiring diagrams and £25 for information on the controller.
Any one else had problems like this? or has any information on the following in awful chillers
RC Group
UNICO A.STD
Model: 142.F2 G7
:confused:
25 quid for a wiring diagramm?
Some rip-off that is...
marley821
02-07-2007, 09:24 PM
Hiya
I have worked on these a few times. Password I am sure is either 9763 or 4763.
They are crap but fairly straightforward.
Probably lost its gas charge from the flexible pipe used on the discharge - they are prone to leaks, I have replaced two in the past and only ever worked on three of them!!!!
Best of luck
Steve
puddleboy3
03-07-2007, 08:00 AM
Hiya
I have worked on these a few times. Password I am sure is either 9763 or 4763.
They are crap but fairly straightforward.
Probably lost its gas charge from the flexible pipe used on the discharge - they are prone to leaks, I have replaced two in the past and only ever worked on three of them!!!!
Best of luck
Steve
Thanks for the replys
Gas charge on both circuits is fine but im having problems with low oil pressure on both circuits.
Circuit 1 only trips on oil pressure when the compressor is running unloaded.
Circuit 2 was tripping on refrigerant low pressure which was down to a faulty expansion valve. Changed and ran up to find that it was tripping now on low oil pressure. Whilst checking over the system noticed what looks like sludge floating around in the oil.
2x simple awful chillers = lots of problems:mad:
kerrcell
13-07-2007, 08:56 PM
Puddleboy3,
have worked several times on rc chillers.Code to enter system is 4763.Regarding the low oil pressure,one should check the refrigerant level in Kpa on both sides of system by using control status.Find fistly compressor 1 and continue pressing.The pressures will be read on the display.If they are low there is a leakage.One should check also liquid line solenoid valve cil run on either 100v or 240v.Check first.Send us back
Kerrcell.