PDA

View Full Version : Excessive Frosting on the Evaporator



vadivelan
22-06-2007, 01:51 PM
Hi,

This is my first post to Refrigeration Engineers. I like to take help from you guys.

In one of our site we have excessive frosting on the evaporator inside the Reach in Cooler. We have checked for door leaks, Defrosting Cycle, Operation of Defros heaters and found O.K.

Could any body tell me what are the other probable reasons for this excessive frosting.

DVaider
22-06-2007, 02:17 PM
Hi, vadivelan. Try to check the volume of the rifregerant in your system. It may be to much. Also try to check the controls of your TEV.

Samarjit Sen
22-06-2007, 03:17 PM
Yes first check the quantity of refrigerant, and the TEV settings. Could you please let us know as to what are the basic products being stored and wether the same are in wet state. What is the door service. Is this Reach in Cooler locally fabricated or the same has been imported.

Excessive frosting could be due to many reasons. If you could provide the above informations and the suction and discharge pressures maybe it would help to find the reason for frosting.

nevgee
23-06-2007, 01:06 AM
.... ............. . . ...

smpsmp45
23-06-2007, 08:42 AM
I have always seen that the drain line is the issue & it needs to be checked for U loop.

claude11
23-06-2007, 12:18 PM
If the product is wet ( my company freezes fish ) , make sure the coils are clear at the start and set your defrost about 1/2 way through the feezing cycle .