PDA

View Full Version : Equal COmpressor



smpsmp45
16-05-2007, 10:22 AM
We are looking at equaivalent compressor

We have L' nite Hermetiq ( france make)
Model : TFH 4540 Z
20 Bar, Min -30 Deg C, Max 48 Deg C, 2500 tr/min & 12.9 cubic meter per hour.

this is a 3 HP compressor, 400v/ 3 Ph, 50Hz Ac operation on R 404A.

We need equivalent Maneurop/Danfoss which are available in India.

Brian_UK
16-05-2007, 07:38 PM
Why not ask the question of your compressor supplier?

ernestlin
17-05-2007, 04:18 AM
Woo, dude. you only need a call to solve your problem..

Peter_1
17-05-2007, 06:32 AM
You need a Maneurop which gives 4486 W at -10°C TE /55°C TC, SH 11K and SC 8.5 K (or 5635 W at -5°C TE, same conditions)
That's all you need to select the proper Danfoss/Maneurop with their Foresee selection program .;)

smpsmp45
17-05-2007, 06:53 AM
Many thanks. Since we do not deal with the compressor directly, we had to get the answers this way.