06-05-2007, 01:00 AM
Anyone have a book on the proper line set size for a 5Ton AC using R410a?
Thanks!....
star882
06-05-2007, 03:42 AM
What's the size of the fittings?
I'm sure it would be designed for the correct size.
Also check the manuals.
hvac01453
06-05-2007, 04:32 PM
You can't always go by the connection size found on the unit or this would eliminate the need for tables altogether. I have tables for R22 but not R410a.
Peter_1
06-05-2007, 09:03 PM
A book about the lines of a 5 ton AC on R410a??
I have a book for a 3 ton and a 7 ton, can this help you any further?
Anyone have a book on the proper line set size for a 5Ton AC using R410a?
Thanks!....
Hi,
I can give you the line size if you tell me the followings :
1- Compressor capacity at design conditions.
2- Horizontal Pipe length (suction, liquid).
3- Vertical pipe length (suction, liquid).
4- Number and type of bends.
I have developed a pipe sizing programme and it is easy to size the pipes.