View Full Version : Ammonia evaporative condenser surface



Gonzalo Arias
14-04-2007, 03:59 AM
Dear Friends:
Does some body knows the surface area required per MBH at manufacturer std. conditions for a evaporative condenser.
Best regards
Gonzalo ARIAS

Lc_shi
17-04-2007, 02:25 AM
It depends on the manufacturing. It is usually from 2kw/m2 ~4kw/m2 . Only for your ref. You can refer to the specific catalogue for it.

regards
LC

Gonzalo Arias
18-04-2007, 05:58 AM
Thanks LC
I think that Vilter, Baltimore, Evapco have about the same surface area, Do you Know this figures? also Kw/m2 that you stated are evaporator KW or total heat rejection KW?
Best Regards
Gonzalo

Lc_shi
19-04-2007, 02:20 AM
The ammonia evaporative condenser total heat rejection:2~3.3KW/M2 usually;we made copper tube evap condenser and the heat reject is at the upper level.
Hope it can do some help for you. You'll design it or manufacture it?

regards
LC

Gonzalo Arias
20-04-2007, 06:58 PM
TK, this will help, we use carbon steel pipe.
Best Regards
Gonzalo