I have problem in prosab Panel with Sabroe screw compressor . We see error on screen (brine low temp. ) and the compressor does'nt run
asking help Thanks

Paulajayne
12-03-2007, 02:21 PM
Not had experiance on that one but I would check the heater, the stat and trips or fuses.

Paula

HGS
12-03-2007, 02:25 PM
Hi.
It seems that you have a broken PT100 sensor or that the connection/cabel is damaged.

Is the Brinetemp showing fx.-200.

HGS

dolce
14-03-2007, 02:41 PM
Dears / Paulajayne and HGS
Thanks for your interested and I'll Check all connection for all sensors
Can you explain what is Brine temp?
I know the Brine is Ca cl2 solution
regards

Paulajayne
15-03-2007, 02:19 PM
Hi

I think a translation problem here.

"TEMP" is short for "Temperature"


Paula