hello . I once knew how an oil pressure differential switch work..could someone tell me again how it works both mechanically and electrically ..the aid of an electrical hook up is appreciated

frank
06-03-2007, 09:20 PM
Hi Chabby

The oil pressure switch is a safety device to protect the compressor.

At switch on it will allow the compressor to run for a set time, say, 60secs, 90secs or 120secs, during which time it is looking for a differential in the oil pressure.
When a voltage is applied to the switch, a small heater is energised that will run for the set time (above) before breaking the compressor control circuit.
If a dp is available on the system (i.e. good oil pressure) then the bellows pressure operates another relay which bypasses the heater contacts and allows the compressor to run.

frank
06-03-2007, 09:31 PM
I tried to edit my previous post but it wouldn't reload.

have a look here http://www.danfoss.com/Products/ProductFinder/ProductFinder.htm?segment=RA&category=http%3a%2f%2fwww.ra.danfoss.com%2fra%2fProducts%2fProductCatalogue.asp%3fNavigation%3dHideO nAllPages%26Footer%3dHideonallpages%26Division%3dRC%26HL%3d1%26TopViewItem%3d92%26AppID%3d%7bc2a95da c-5e01-47df-92cd-5972d837cf1a%7d%26dyn_lang%3d

chabby
07-03-2007, 01:54 AM
thanks very much Frank....the info helped..