01-03-2007, 12:25 PM
G'day all
I am having trouble with a Panasonic cassette model number as above.
There are two seperate units ran off the one controller.
Had the unit set for cooling 16 degrees c to test operation but could only still get one unit to operate.
From the limited information that I have it instructs me that I can look up previous faults by holding down the check button on the controller.
The previous faults were:
Unit No 1: F30 (open or reverse phase)
Unit No 2 F26 (communications error between controller and indoor unit).
From what I understand "CHECK" has to be flashing if a fault is current.
LED's on the outdoor unit are numbered 1-8 and the only one that is lit is LED 1,which I presume is telling me that the board is ok.
Unit operates OK on test mode (cooling and heating].Which is making me suspicios of the ambient air sensor of the indoor unit.
Unit had been running as the compressor was quite warm.
Thanks in advance.
I am having trouble with a Panasonic cassette model number as above.
There are two seperate units ran off the one controller.
Had the unit set for cooling 16 degrees c to test operation but could only still get one unit to operate.
From the limited information that I have it instructs me that I can look up previous faults by holding down the check button on the controller.
The previous faults were:
Unit No 1: F30 (open or reverse phase)
Unit No 2 F26 (communications error between controller and indoor unit).
From what I understand "CHECK" has to be flashing if a fault is current.
LED's on the outdoor unit are numbered 1-8 and the only one that is lit is LED 1,which I presume is telling me that the board is ok.
Unit operates OK on test mode (cooling and heating].Which is making me suspicios of the ambient air sensor of the indoor unit.
Unit had been running as the compressor was quite warm.
Thanks in advance.