View Full Version : Cable tray for refrigerant Piping



harsen
07-02-2007, 07:57 AM
Can anyone tell me about the fixing standard for

tray in the riser and in roof for refrigerant piping for

ducted split Unit


Senthil

Brian_UK
07-02-2007, 07:23 PM
Fixing distances are the same regardless of what the pipework is being fixed to.

Pipework should be insulated and any brackets/clips etc should also be insulated.

adams?
08-02-2007, 06:26 PM
not sure about your country but genral standard in uk is 1.5 metres between fixings

malik55
08-02-2007, 06:43 PM
Harsen
you can free down load some info for cable trays from http://chalfantcabletray.com/uploads/pdf/specs_NEMA_Ve2.pdf
malik55

michael7
09-02-2007, 05:02 PM
Don't tie wrap the pipe to the tray in the riser, as the pipe could slip inside the insulation and cause a probelm with the vapour seal. If you pull the tie to tight it will cause a failure of the insulations integrity.
Best to clip with Insualted HYDRO-ZORBS or CUSH-CLAMPS on channel.

harsen
13-02-2007, 02:02 PM
Thank you malik for the link , its very useful to me


Senthil