View Full Version : york recip chiller model ydaj77xt9
kolab technical
04-02-2007, 11:53 AM
i am commissioning this chiller, and it is displaying [REPROGRAM TYPE OF REFRIGERANT TO RUN].I've evacuated and recharged with R22 meant for the unit,yet the signal does not disapear and unit not start.Pls help out to reprogram refrigerant type.
kolab technical
04-02-2007, 11:55 AM
pls reply quickly
Check your dip switch settings, i think it's the first one.
al
Quality
05-02-2007, 09:12 AM
I will second that one:)
If you press the options button on the micro it will list the programed options in order as they are for the dip switches inside.
nebbie67
06-02-2007, 04:12 PM
hi kolab
You must press "options" button, note the position of refrigerant selected string and operate on the same dipswitch in the main electronic board inside control panel. The two value must match. Look, if this alarm occurred in a used chiller, a memory problem could be present (that's a real damage, try to think at motor current set.....). If group is new and this is the first start up, well... can be !
Good luck !
valibrinza
24-08-2010, 06:15 PM
HELLO!how you solve the problem with the message REPROGRAM TYPE OF REFRIGERANT TO RUN, what code is about?my chiller is york millenium ycas0503.thanks!
yorkie10
26-08-2010, 12:32 PM
Dont panic - it doesnt sound terminal. Program settings are held in CMOS memory and as such are backed up by a battery, these batteries have, approx, a 10 year life span, if its failed and the main power is removed from the micro board ALL program settings, including refrigerant type will revert to their default settings, however to get the chiller to operate you will have to be re enter these settings through the program button
bratosin
10-01-2011, 06:55 PM
Hi guy can you help me whith a suplier for spare parts for this tipe of chiller . I have problem whith temperature sensors. thanks a lot.
johnson controls can supply you or give me the details and i can post some over to you.