View Full Version : Frequrency conversation technology & a normal rotatory compressor



ernestlin
08-01-2007, 07:00 AM
Dear Advanced sirs:
If frequrency conversation technology can be applied to a normal rotatory compressor?Is that possible? If it's feasibility, please tell me what it should be considerated? Thanks a lot for any input!

NoNickName
08-01-2007, 09:00 AM
I assume that by "frequency conversation" you mean "variable frequency driven" compressors.
The short answer is yes, though you have to contact your compressor manufacturer for checking the operation envelope and limits.

ernestlin
10-01-2007, 06:56 AM
Thanks, Nonickman. If a normal rotatory compressor work under a lower frequency, is there any negative influnence on the oil supply?? As I know, the oil is supplied by a centrifugal oil pump in hermetic compressor, and the pump is driven by the motor.

rgds
Ernest

NoNickName
10-01-2007, 07:30 AM
Yes, there is a negative influence on oil return. I normally set my inverters to run at full speed for 30s every 10 minutes to ensure oil return.

nebbie67
19-01-2007, 01:40 PM
There's a lot of variables to discuss to, in order to establish minimum rotation speed. First of all, if you talk about an hermetic or semi-hermetic compressor, you must consider minimum flow of refrigerant in the suction necesary to cool down electr motor windings, and if the windings are wrapped to support an VFD use (wires insulation). And, over this, don't forget problems regarding harmonics distorsions on the electrical lines that usually an inverter can generate.
It seems not so simple, isnt'it ???

ernestlin
29-01-2007, 02:57 AM
Yeah, very detailed suggestion, thanks! nebbie. I totally agree with your opinions, and will consider them throughly. It's really a complex problem, so the various experiments may help me slove it. : >

Electrocoolman
31-01-2007, 12:24 AM
Another point is that the compressor needs to be 3 phase type. Speed control cannot work on 1 phase compressor, though you can get a VSD for single phase supply.

NoNickName
31-01-2007, 08:03 AM
The unit can be designed with single phase supply and single phase inverter, but then internally three phase will run between the inverter and compressor.