02-01-2007, 08:10 PM
Hello everyone can you advise me a drop in for a walk in running on R12 operating as a chiller 40-45 deg f
Thanks

Andy P
02-01-2007, 09:53 PM
Hi Mike - you could try DuPont's ISCEON MO49 which will act as a drop in. It is mainly targetted at car a/c but will work fine in your application, and is particularly good in higher ambients. There are also others if you can't find a DuPont stockist, but make sure you use something compatible with mineral oil

cheers

Andy P

Raven
02-01-2007, 11:29 PM
Hi Mike,
R409A is what we use here in London as a drop in for
R12 not that there is a lot of use for it now.

Hope this helps,
Cheers,
Raven

bobkellyb
03-01-2007, 11:34 AM
There several to choose from, I have found R409a ok
but latley have been using SP34E, (134a with some additives so it can be used with mineral oil)

mikejen
03-01-2007, 01:25 PM
Thanks everyone will need to get the Refrigerant from the States as no one on the island has the Refrigerants you have mentioned