View Full Version : Refrigerant volume



Nirmalya
02-10-2006, 10:34 AM
Looking for some knowledge on the following points. Consulted many books but no clear explainantion.

1. How to calculate optimum refrigerant volume requirement for flooded chiller ?

2. When chiller is out of operation or is stopped, do all ***** from condenser get accumulated in evaporator and stays there. Any ***** gets locked up in condenser ?

3. Is there any allowable limit of oil ***** mixing in evaporator ?

Lowrider
02-10-2006, 09:24 PM
The optimal charge depends on the length and size of the liquid lines.

If no solenoidvalves are placed the ***** will go to the coldest part of the system, thus the evaperator!

US Iceman
03-10-2006, 01:24 AM
Nirmalya,

If you do some seraching in the RE site there were several threads discussing the refrigerant charge calculations for flooded chillers.