PDA

View Full Version : Evaporator freezing up


Cooler
31-08-2006, 09:25 PM
I guess their are probably a host of reasons why this happens but one suggestion on another forum states that the system running low on gas will cause the evaporator to freeze up .
I would be very gratefull if you learned gentlemen could confirm if this really the is the case .
Kind regards.

Cooler
31-08-2006, 09:28 PM
Its a small A/C system by the way.

Brian_UK
31-08-2006, 10:34 PM
Yes a shortage of refrigerant will lower the operating temperature and cause the evaporator to freeze up.

The operating temperature of the coil should be above 0°C at least with A/C.

Bones
01-09-2006, 11:15 AM
if its an ac system and your frosting up the indoor head on cool mode you most likely lost refrigerant - also check liquid line coming back to condensing unit if this is frosted also is sign.

DEVIL
01-09-2006, 10:00 PM
frosted up indor usualy means low on refrigerent, but, u should make shore 1rst that the fun is blowing, filters clean, and if the evaporator isn't dusty that could make the air flow gow down, and frust the indor unit

TXiceman
02-09-2006, 03:26 AM
You can also get a freeing coil condition with reduced air flow. Better check this issue first.

Ken

frank
02-09-2006, 01:51 PM
You can also get a frosted / frozen evaporator when the expansion device is a capillary and the unit is operating in low ambients without head control

Soumo_roy
02-09-2006, 05:15 PM
:) :eek: :mad: :cool: :p :D :o :( i know

Brian_UK
02-09-2006, 10:56 PM
:) :eek: :mad: :cool: :p :D :o :( i knowYou know what ?
Would you care to share ?

Cooler
03-09-2006, 02:15 PM
Thanks Guys.:)

Samarjit Sen
05-09-2006, 02:51 PM
Check the fan. Reduced air can cause frosting on the coils.

TXiceman
06-09-2006, 01:32 AM
Check the fan. Reduced air can cause frosting on the coils.


I already said that....:D

Ken

Samarjit Sen
06-09-2006, 01:47 PM
Thank you. I also had eactly similar problem, and by increasing the air volume, the plant started maintaining the desired conditions and every thing was normal.