Cofreth
28-08-2006, 01:27 PM
I have a problem with a Mitsubishi Heavy Industries VRV system. Condensing unit malfunction,control card green light blinking,inverter card green light blinking and LED3 lighted,contactor energise but nothing in the condensing unit is running.There is voltage at compressor terminal,each cable to Neutral reading 300Volt except one cable reading only 40 Volt AC current.After inspecting all other component,found power transistor top part cracked.Suspect that is the fault,replace a new set of power transistor,system and compressor run,check compressor running amp, one cable 21amps,another 16amps and last cable 7amps only,is this normal?After running this air-con unit 24 hours for 2 days,system down again, found 2 pieces of porcelain resistor burnt,advice from distributor to replace the porcelain resistor and diode too.After replace the above parts,before turn 'ON' power, found inverter PCB one of the circuit sending signal to power transistor the tiny transistor was burnt. Therfore,I went back to the distributor and purchase a new inverter card,after fix in the new inverter card and turn 'ON' the power,observe the green light from inverter card blink for few seconds,again the tiny transistor of the new board burnt again. Anyone has any clues about this problem? Thank you.