View Full Version : Condensor freez up



wolf
09-08-2006, 10:27 AM
Hi guys
I have problem whit condensor on a/c unit its aicing up ,checked gas level ok. What is the best way to check revrcing valve i know by resictence bat what should be reading on my multi meter?

MadApprentice
09-08-2006, 12:52 PM
what is the ambient temp and humidity where you come from?

Brian_UK
09-08-2006, 11:13 PM
Come on Wolf, give us a clue, what make and model of unit is it ?

You say that the gas charge is OK and then suspect the reversing valve; are the temperature across the reversing valve OK, does the slide operate ?

Josip
09-08-2006, 11:41 PM
Hi, Wolf :)

Maybe I am not right but...

It is winter time now in Autralia, you use you A/C for heating. It is very easy to have too much humidity and your condenser/evaporator is frozen.

Maybe your defrost function is not working properly...

Best regrds, Josip :)

wolf
10-08-2006, 12:13 AM
ok hahaha Airwell ,model cds110h ,R22 refrigerant
Temperature accros revrsing valve is ok, slide operate,high humidity,system on heating and unit is aicing up? (refrigerant charge 100% ok)

Brian_UK
10-08-2006, 03:17 PM
Sounds like a defrost problem then Wolf.

Langer
12-08-2006, 12:17 AM
Could be the outdoor temperature sensors.

Peter_1
12-08-2006, 03:56 PM
[QUOTE=(refrigerant charge 100% ok)[/QUOTE]
How do you know?

MadApprentice
12-08-2006, 04:44 PM
yes, how do you know, unless you weighed the gas out ? i am sure they dont have sight glasses and to say the gas is ok off pressures, they tell me you shouldnt do that?

cool breeze
12-08-2006, 07:02 PM
It's normal to see some frost on condensor coils in the heat pump mode below 35 deg. just befor it drops into defrost. If the system is charged properly than the coil will defrost in a couple of minutes. In high humid areas the melting frost can accumalate at the bottom of the condenser and refreeze. Check to see that the unit is elevated high enought for the water to leave the unit and holes in the bottom are clear of leaves or trash so water can drain free. If this is all good than the problem is the defrost controller or the thermister.

wolf
14-08-2006, 09:04 AM
How do i now?(gas 100% ok) installed sight glass!

frank
18-08-2006, 11:17 PM
Never charge to a full sight glass without taking pressure/temperature readings to confirm your opinions.