Hi
I bought a Gram plus F660 L used freezer recently. The problem is that it donīt go below -9 C.
The cold side of the compressor gets full of ice. The refrigerant is R290. Both fans inside and outside are working well. ANy sugestions?
Sven
:o

The MG Pony
06-08-2006, 05:23 PM
Sounds over charged, was it orrigionaly R-22 then converted over?

If so then over charged as you need so litle with R-290

Abe
06-08-2006, 10:20 PM
Hi
I bought a Gram plus F660 L used freezer recently. The problem is that it donīt go below -9 C.
The cold side of the compressor gets full of ice. The refrigerant is R290. Both fans inside and outside are working well. ANy sugestions?
Sven
:o


Please explain what you mean by the cold side of compressor?

Yes, true , the low side does return evaporated gasses which are cool...........but if the pipe is iced over......as previous poster has mentioned.........overcharge is likely

wallwall
06-08-2006, 11:06 PM
Itīs loaded with r290 from the beginning.
Somebody has filled it before I get it! I dontīt know who it was or what he used to fill it.
Clean it and rechargehttp://www.refrigeration-engineer.com/forums/images/icons/icon6.gif

The MG Pony
06-08-2006, 11:10 PM
Ja that would be my sujestion as well, Vac, new Filter dryer, new oil (Why not certainly will not hurt) and a properly weighted in charge, that will have a purring away (I wuve R-290 :) )

frank
07-08-2006, 09:53 PM
have you tried DEFROSTING it?

The MG Pony
07-08-2006, 09:57 PM
One would tend to immagine it would defrost rather well durring transport, but non the less a good idea to duble check.

wallwall
08-08-2006, 04:52 AM
Yes, it was completly defrosted, about +30 C