http://www.refrigeration-engineer.com/forums/images/icons/icon1.gif High cool problem
Has any one had any dealings with high cool. I've installed a u ceiling mounted unit. i'm getting a fault where the 32 amp breaker is arking i have used 2.5 t+e and 1.5 interconnecting the unit itself was running fine and i had a call to say the ac had taken out the dist board. i took the 32 amp breaker off and it was all carbonised and the dist board is u/s. I managed to get a tempory supply and meggered the unit all fine. But the amps are 19.7 (running) instead of 7.1. When commisioned they were 7.4 i've checked the unit over and all seems fine. Any ideas:confused: :confused:
Has any one had any dealings with high cool. I've installed a u ceiling mounted unit. i'm getting a fault where the 32 amp breaker is arking i have used 2.5 t+e and 1.5 interconnecting the unit itself was running fine and i had a call to say the ac had taken out the dist board. i took the 32 amp breaker off and it was all carbonised and the dist board is u/s. I managed to get a tempory supply and meggered the unit all fine. But the amps are 19.7 (running) instead of 7.1. When commisioned they were 7.4 i've checked the unit over and all seems fine. Any ideas:confused: :confused: