View Full Version : Airwell



wolf
27-07-2006, 10:48 AM
What is the best way to check Airwell unit?
i mean there is no contatctor no lights on pc board?
I turnd on circle breaker unit strats strait awey on cooling and i want heating . replaced pc board indoor unit still doing it?

NoNickName
27-07-2006, 12:24 PM
Airwell are only working in the northern emisphere, so in summer they start cooling. :-)

ConDor
27-07-2006, 04:43 PM
What model is it?

wolf
28-07-2006, 10:06 AM
hmm its got revrcing valve so that means its working on heating too but the problem is when i turn circle braiker on unit starts on cooling. my question is why the unit starts on cooling and i set remont control on heating.(i replaced pc board) i just want to now what starts unit?

Andy W
28-07-2006, 04:43 PM
Is it to warm to call for heating?

Ian Neill
28-07-2006, 07:51 PM
Hi cool and heat signal comes from indoor pcb make sure you havent got a relay which is sticking on the board.... These are the worst units i have ever worked on.sorry cant help any more than that

Toolman
29-07-2006, 04:42 AM
These are the worst units i have ever worked on.sorry cant help any more than that

Yes Airwell is one of the worst we could start a new thread for the worst brand .:mad:

Heres a basic question for the no heating AIRWELL because I would look at this first , is there power to the reversing valve when its calling for heating ? Could be as simple as that a stuffed coil on rev valve. :D

wolf
30-07-2006, 08:57 AM
thanks to all of you