10-07-2006, 11:02 PM
Hi people been around for a short while but never posted so
its my first time be gental please! i have been working on a
semi perment trailer which has a small fujitsu a/c installed AOY25 all is well when im on site but intermittently it trips the breaker 25a d rated rcd, the supply comes from a 75a diesal genarater 225v checked cappy all ok start amps around 60a peak hold on amp clamp, wondered if genny has to much load but why would that trip my a/c breaker?:confused:

Brian_UK
10-07-2006, 11:41 PM
Hi, welcome, yes the start load could trip things as the voltage will drop and the amperage will rise to compensate.

tait71
11-07-2006, 08:41 PM
hi just an update, checked over today and the genny voltage is very unstable we are going to get a contractor to check the genny and report back i have also learned that the a/c has never tripped on a land power supply, worth knowing.

cheers
tait71

John Wood
15-07-2006, 12:03 AM
Is it tripping on RCD or MCB????

tait71
17-07-2006, 08:25 PM
its tripping an rcd d20 but the genny is loosing voltage on comp start, once the genny is sorted i will post and let you know whats happening then. cheers:)