09-07-2006, 09:10 PM
Ever wonder what makes a 13 seer different from a 10 seer? I have-and what I've seen from my experience is a difference in the surface area of the coils. I saw a 10 seer Carrier side by side with a 13, used the same compressor, but the condenser was physically larger. Is that all it amounts to? If so, what are the limitations of compressor-to-condenser sizes, i.e., could you use a 3 ton compressor in a 5 ton condenser (for a 3 ton load), and expect a higher efficiency?

NoNickName
10-07-2006, 07:39 AM
Yes, the bigger the condenser, the higher efficiency expected, provivided SC is within manufacturer spec.

Stoofer
16-07-2006, 09:49 AM
Hi Guys, would this same principal make an inverter twin split more efficient when only running one of the indoor units?

Andy
16-07-2006, 09:54 AM
Hi Guys, would this same principal make an inverter twin split more efficient when only running one of the indoor units?

Yes and no:) the larger condenser would be good and the lower speed of the compressor should be more effecient, but that would depend on the compressor selection:)

Kind Regards Andy:)

frank
16-07-2006, 09:58 AM
Hi Guys, would this same principal make an inverter twin split more efficient when only running one of the indoor units?

You can't "only run one of the indoor units" on a twin split. You can on a multi system.

Stoofer
16-07-2006, 10:36 AM
Sorry was meaning Multi split I've been looking at a few sysytems with the view of heating/cooling my conservatory and living room, anyone got views on these systems Mitsubishi SCM45ZD Vaillant V6-060 M2N and I belive Tosh now do a Daiseikai 2 though this maybe beyond my buget.

Andy
16-07-2006, 11:22 AM
Sorry was meaning Multi split I've been looking at a few sysytems with the view of heating/cooling my conservatory and living room, anyone got views on these systems Mitsubishi SCM45ZD Vaillant V6-060 M2N and I belive Tosh now do a Daiseikai 2 though this maybe beyond my buget.

The Daiseikai is the most effecient on the market at the moment:) The RAS 10 has a COP of 4.51;)

Shop about this is a domestic product and as such should be affordable, try another supplier:)

Kind Regards Andy:)

Stoofer
16-07-2006, 11:36 AM
Cheers for the advice Andy that COP really appeals to a double tight Bas***d like me :)

Andy
16-07-2006, 12:07 PM
Cheers for the advice Andy that COP really appeals to a double tight Bas***d like me :)

No prob:)

just to note that COP is mid range, these units about 2.5kW in this case. Range is 0.5 to 3.5kW.

Try and select your unit at required duty in this sweet spot:)

Kind Regards Andy:)

Stoofer
16-07-2006, 09:06 PM
Sorry to be a bit dense Andy , are you saying if my room requires 2.5kw of duty fit a 3.5kw unit and it will run more effiecently in it's mid range?

I should have the signature "If it's too hard i can't understand it" :)

Peter_1
16-07-2006, 09:50 PM
I don't know if Andy meant this but selecting a larger indoor unit is mostly a good solution.

In a non-inverter situation, unit will evaporate higher, so COP will increase.

With an inverter, heatload can be 'absorbed' at a lower speed, so reducing noise. At partial load, compressor will run sooner on a lower speed increasing it's COP.

Also less wearing on the compressor bearings.

When I started many yeras ago, when we installed a Daikin, we allways ordered a bigger indoor size then the outdoor unit.

When is it not a good solution? For those who lives in very humid climates and need to dehumidificate a lot.

Stoofer
16-07-2006, 10:17 PM
Cheer's for the explanation Pete, I'm gonna take Andy’s advice and shop around for a Daiseikai 2 to supply my living room and conservatory, the room unit will get much more use so I'll go for next size up now as dehumidifying isn't really necessary for me.

Andy
16-07-2006, 10:26 PM
Cheer's for the explanation Pete, I'm gonna take Andy’s advice and shop around for a Daiseikai 2 to supply my living room and conservatory, the room unit will get much more use so I'll go for next size up now as dehumidifying isn't really necessary for me.

With inverter units the book value at the greatest COP is the one to go for.

If your room needs 2.5kw a 2.5kW nominal inverter is the one to go for, it already has the over sized indoor, a the 2.5kW will do 3.5kW maximum:)

Kind Regards Andy:)

Stoofer
17-07-2006, 01:04 AM
ok cheers for info guys.

star882
23-07-2006, 05:06 PM
When is it not a good solution, for those who lives in very humid climates and need to dehumidificate a lot.
Use a two speed indoor fan and switch it to low when the humidity is high.