If your Thermal Expansion Valve and distributor lines are icing but your walk-in is warming above setpoint, what are the first things that should come to mind in terms of diagnostics?

I just figure it is low on refrigerant but could somethin be wrong with the design?

We're talkin 2HP Copeland w/ r134a for a 4c room.
TXV is Alco with MOP thermal bulb charge.

Thanks folks, Joe.

NoNickName
28-06-2006, 04:14 PM
1) Low on gas. Check SH, SC and eventually fill it up.
2) Liquid solenoid blocked. Change diaphragm.
3) Liquid filter clogged. Replace core.

Andy
28-06-2006, 06:37 PM
1) Low on gas. Check SH, SC and eventually fill it up.
2) Liquid solenoid blocked. Change diaphragm.
3) Liquid filter clogged. Replace core.
4) Lack of subcooling, poor refrigerant quality after the expansion valve

Kind Regards Andy:)

wambat
28-06-2006, 07:27 PM
Strainer on inlet of TXV partially plugged

frank
28-06-2006, 07:29 PM
If your Thermal Expansion Valve and distributor lines are icing but your walk-in is warming above setpoint, what are the first things that should come to mind in terms of diagnostics?
Obviously the evaporator is not full of liquid and so the duty is reduced. Why it is not full of liquid is subject to investigation.

liptow
28-06-2006, 08:01 PM
Thanks all.
And Frank, can I be in your foursome?
Joe

frank
28-06-2006, 08:16 PM
Thanks all.
And Frank, can I be in your foursome?
Joe

have you got any clubs? :D

Peter_1
28-06-2006, 08:26 PM
What's a 4c room? I personally like more a 5 W room :D
Pressures readings?
Temeprature readings SH and SC?