PDA

View Full Version : compressor running dry


daleworne
16-06-2006, 11:08 PM
i have a general question. What happesn say when u have a leak and all the refrigerant leaks out and then u run the compressor.

What will happen? Will this damage the compressor

r600a-bang
16-06-2006, 11:34 PM
pending on how long it has been running, remember the compressor needs cool gas down the suction to keep the windings cool. i have known compressors to run and cycle on the klixton until an engineer has arrived but over a short time the compressor will be damaged

r600a-bang
16-06-2006, 11:37 PM
and yes normally the sight glass should be clear but you must attach your gauges to find out if the system is completely void of refrigerant

chemi-cool
17-06-2006, 08:56 AM
there should be a low pressure control to protect the compressor from such events.

Chemi:)

daleworne
17-06-2006, 11:16 PM
thanks for the replies