PDA

View Full Version : Phoenix Carrier Reefer Unit Trouble



razorback76
16-06-2006, 09:10 PM
I have a 96 Phoenix Carrier Unit that I'm needing some help with. This unit has worked just fine the last 6 months but I let it set for 10 days without running it and now it won't cool down. Coolant reaches 150 after about 10 minutes or so, and the suction line is reading -5 to -6. I really just don't have a clue and any help would be appreciated.

novel.harris
17-06-2006, 02:59 PM
hello am Novel and am in Afghan with a model 69nt40-5013 reffer manufa. 4/95 need help to clear alarm 52 it will not start am in the army a need help.

Iankp
19-06-2006, 12:45 PM
Make sure that there are no other active alarms other than AL52 (alarm list full) in alarm list.
Select "Alt Mode" parameter "DC30" and press enter for 5 seconds to zero trip start then clear alarm list as normal.

Best Regards
Ian

Reeferjon
22-06-2006, 10:47 AM
Possible shaft seal leak on the compressor resulting in loss of refrigerant....is there a lot of oil round the shaft that enters the compressor......you will need to fit gauges to check pressures.

John.





I have a 96 Phoenix Carrier Unit that I'm needing some help with. This unit has worked just fine the last 6 months but I let it set for 10 days without running it and now it won't cool down. Coolant reaches 150 after about 10 minutes or so, and the suction line is reading -5 to -6. I really just don't have a clue and any help would be appreciated.

razorback76
11-07-2006, 07:39 PM
thank you reeferjon!